CC,
An NCR and a good kick in the ass are the first two that come to mind.
You don’t mention the thickness of the structural column or whether correct preheat was applied.
If I was the client I would be requesting hardness testing if it was a thick column.
Have you performed MT as a minimum on the weld ?
Regards,
DD
Hi there CC,
You have put the cart before the horse, you should have an approved WPS to work to, what happens now if the test fails?
You will have to assume the weld on the column is un acceptable as well.
AS1554.1 does allow you to qualify a PQR from a production weld but you are running a risk in doing so MMAW isn’t too bad but if you were using GMAW that would be nuts.
Cheers!!
I must agree with the previous two comments on this post. There seems to be an increasing trend to take the pathway of least resistance when it comes to compliance with welding standards in Australia.
The question that you must ask yourself when interpreting any standard or statute legislation, is what is the intent of the document that you are interpreting.
With AS 1554.1-2011 one of the main area that catches contractors out is clause 1.7.2 Basic welding requirements.
Attached is Appendix D from the current version of the standard, looking forward to the 2013 draft the appendix and clause quoted above have not changed.
If these two fundamental items are addressed, compliance with the Standard and Principals requirements will be achived much easier, without heartache and loss of professional reputation